Posted By: Trumpy Multiple feeds, One Service - 07/05/05 04:45 AM
Submitted by renosteinke:

Quote
For some reason, the PoCo ran two sets of wires- a set of 2/0 and a set of #2 for one service. You can see how the wires are spliced.
Ordinarily, there would be two insulated wires for their 120/240 service, as well as the bare ACSR neutral.

[Linked Image]
Close Up
Posted By: Trumpy Re: Multiple feeds, One Service - 07/05/05 09:35 PM
Hmm,
I always thought that PoCo's were all for saving every cent possible?.
{I know the one I work for does!!} [Linked Image]
The extra wires wouldn't by any chance be for future expansion would it?.
Is this a Residential or Commercial installation?.

{Message edited to add some missing letters} [Linked Image]

[This message has been edited by Trumpy (edited 07-05-2005).]
Posted By: renosteinke Re: Multiple feeds, One Service - 07/06/05 01:25 AM
The location is commercial, with separate meters for two stores. Below the mast is a gutter, with taps to four meters (each business has separate meters for the hot water), so this service has been there a while.

Despite there actually being two services, the practice here is to use a gutter to tap off of one set of wires. That is what was done here.

Future expansion? The PoCo would upsize the transformer, and run larger wires.
Parallel feed? The PoCo would run wires of the same size. Different sizes run in parallel are, well, a really stupid thing to do. (If someone out there doesn't understand 'why," speak up and we'll explain it!)
The method of connection is concealed by the tape over the splices. The usual connector here is a "parallel groove" type, with grooves for two wires, not three. PoCo rules do not allow the use of split bolts.

The PoCo itself is a little confused as to how this happened. When they fix it, I'll have a Sunday service change to do.
Posted By: dmattox Re: Multiple feeds, One Service - 07/06/05 02:48 AM
Its easy to figure out, the PoCo is stealing electricity from itself!!! [Linked Image]
Posted By: ShockMe77 Re: Multiple feeds, One Service - 07/23/05 02:57 AM
(If someone out there doesn't understand 'why," speak up and we'll explain it!)

Ok, I'll bite because I don't know everything.

I understand that it's wrong, but why?

Btw, what does POCO stand for?

[This message has been edited by ShockMe77 (edited 07-22-2005).]
Posted By: chipmunk Re: Multiple feeds, One Service - 07/23/05 01:01 PM
PoCo = Power Company

Got me for a few weeks when I first joined the forum too [Linked Image]
Posted By: Alan Belson Re: Multiple feeds, One Service - 07/23/05 03:20 PM
Did'nt 'sparky 66' coin the word POCO?
Posted By: renosteinke Re: Multiple feeds, One Service - 07/23/05 10:22 PM
The reason this is wrong is because of voltage drop.
Ohm's law tells us that voltage equals the current times the resistance.

Let us assume, for the sake of this discussion, 200 amps flowing, at 120 volts (to ground) over 100 feet.
For #2 wire, table 8 in the NEC give a value of 0.0194 ohms resistance for this length. 200 amps x .0194 = 3.88 volts "dropped". Of the 120 volts that leaves the pole, only 116.12 makes it to the meter.

For 2/0, the value given is 0.00967. 200 x .00967 = 1.934. So, at the meter, 118.066 volts are received.

Wait- one wire is delivering 116 volts, and the other is delivering 118? Right- there's a 2 volt difference.
And, since voltage flows from higher to lower, two volts (400 watts) will flow into the smaller wire.

400 watta is a significant amount of heat generated where these wires meet.

That is why we use identical size- both in diameter and length- for parallel feeds. We eant to avoid setting up this type of situation.
Posted By: John Crighton Re: Multiple feeds, One Service - 07/24/05 06:46 AM
Reno, I don't understand your explanation.

You've described 200 A flowing in each wire, but in fact, the 200 A would be divided between the two according to the ratio of their impedances.

Given your example, that ratio is (.0194 / .00967) = 2:1, so 133 A of that 200 A would flow in the 2/0, and 67 A in the #2. The voltage drops therefore are equal, and there's no power "flowing" from one wire to the other.

Argument #2: A 2/0 wire is made up of 19 strands. Isn't that the same as an 18-strand wire in parallel with a 1-strand wire?
Posted By: SparksNmore Re: Multiple feeds, One Service - 07/24/05 02:21 PM
That's the way the PoCo used to do years ago when they were doing away with residential 3 phase around here and we were replacing the old 3 pase A/C's with new single phase units.
They would parallel the two old service drops into one single phase drop.



[This message has been edited by SparksNmore (edited 07-24-2005).]
Posted By: renosteinke Re: Multiple feeds, One Service - 07/24/05 03:29 PM
John,
First of all, I don't think stranded wires can be considered as "parallel" conductors, (or 'multiple conductors under one lug, for that matter) as they are in constant contact with each other through their entire length. Were they to be individually insulated, you might be on to something.

As to your first point, I suspect that this effect is ignored in your usual electronics class (when doing resistor calculations) simply because it is considered insignificantly small, both in terms of the currents involved and the physical spacing. Those simple calculations also ignore the effects caused by the current being AC, and treat it all as DC.

But- just as those electronics do get warm- improperly paralleled conductors do get quite warm at their termination.

Now, I hve never deliberately created this sort of situation. NEC 310.4 tells us that:
"The parallelled conductors ....shall comply with all of the following:
(1) Be the same length
(2) Have the same conductor material
(3) Be the same in circular mil area
(4) Have the same insulation type
(5) Be terminated in the same manner"


If we could assume that "things would somehow balance out" by dividing the load between the conductors proportionally, then we are left without an explanation for either the heating that occurs, or 310.4.
Maybe there's a better explanation out there, but I've done my best :-)
Posted By: ShockMe77 Re: Multiple feeds, One Service - 07/25/05 12:03 AM
Reno, thank you for that explanation. I really do appreciate understanding why it is wrong. Thank you very much.

Ron
Posted By: John Crighton Re: Multiple feeds, One Service - 07/25/05 04:24 PM
Reno, thanks for the reminder about 310.4. I think the most frustrating thing about studying the NEC is that there are so many rules for which no rationale is stated, even in the handbook.

I suspect the restrictions on parallel conductors have a lot to do with termination methods. Trying to connect two wildly different-sized wires into one terminal could lead to some "creative" and dangerous solutions.

Fault tolerance was probably also a concern. In your hypothetical 2/0 and #2 example, the loss of continuity in the 2/0 would leave all the current flowing in the #2, which would reduce it to glowing slag. At least if the conductors are equally sized, the overload is limited to 2:1.

I believe you when you speak from experience that unequal-sized parallel wiring produces heat at the junction, but there's got to be some other mechanism at work -- possibly higher resistance in the joint itself because of unequal pressure on the conductors.
Posted By: renosteinke Re: Multiple feeds, One Service - 07/26/05 12:57 AM
Thanks for the nice reply, John

Even if a man started in this field the same time as Tom Edison, there are sure to be things he hasn't dealt with very often, if at all. Those things he may not be very "expert" at.

I remember being taught way back about the correct way to make a parallel feed. I have, over the years, even run a few. But- and this underscores my limitations- I have never, ever seen a parallel feed done wrong before this one! So I really can't say, from personal experience, just how horrible it is to make this error.

Now, the PoCo trains its' folks extremely well, and they never, ever improvise or cut corners. (All it takes is a stay somewhere outside the USA to find out -the hard way- just how reliable our grid really is!) So, when I went to them with this pic, I had the entire engineering department saying "Huh?" and scratching their heads. It would seem that this sort of thing is beyond their experience as well.

My grasp of theory might be overly simple, and incomplete- but then who really "understands" those electrons anyway? (I want to study probability theory, I can go to the local casino!).
As I read the code, this sort of thing is a very big "no-no," and that's enough for me to know!

Anybody has a better explanation, please share it with us. I mean that.
Posted By: wa2ise Re: Multiple feeds, One Service - 07/26/05 03:41 AM
A possible reason for requiring the same type and size wire for paralleling might be that a wire that has twice the cross sectional area of another wire will have half the resistance of the smaller wire. And will take 2/3 of the current being demanded by the load. Problem is that the heavier wire has less surface area per amp of current to get rid of the heat due to wire resistance. SO the heavier wire will get hotter. You've seen this in the ampacity tables of various gauges of wire.

Thus the code requirement that paralleled wires be of the same size, etc.

As for the POCO service, I wouldn't be suprised that the linemen didn't have heavy enough cable for that customer on the truck, and there being pressure from the boss to get the customer on line, just paralleled 2 cables to get it done. Management can get that way... [Linked Image]

[This message has been edited by wa2ise (edited 07-25-2005).]
Posted By: winnie Re: Multiple feeds, One Service - 09/05/05 10:55 AM
I know that this is an old thread, but I think that wa2ise has hit it on the head. The ampacity of a conductor is set by the combination of heat produced by the conductor, and heat which escapes through the insulation. Larger conductors have less ampacity per unit of copper cross section because for a given cross section there is less circumference through which the heat could escape.

If you want to see just how big a difference, compare the total ampacity of a single #2/0 conductor with 16 #14 conductors in parallel (separated for good heat dissipation). This is a approximately the same total amount of copper. If you could actually run the conductors at their thermal ampacity limit, you would get more than twice the current through the parallel #14s. (Note: this would not work or be safe for other reasons, and would violate a bunch of codes...just focusing on the thermal ampacity of an extreme example.)

Which leads to a thought about how to save some copper: build rope core cables where you use some sort of plastic filler material covered with copper and then covered with insulation. If you made something that had the external surface area of a #2/0 conductor, but the copper content of a #2 conductor, then my guess is that you would see a thermal ampacity perhaps 20% better than a #2 conductor, I'm guessing the equivalent of increasing the wire size by 1.5 gages.

-Jon