Looks like clearance for the drop from the upstairs window wouldn't be adequate if it was moved to avoid the shutter. (Art. 230-9 1999 NEC)
Also, clearance from the facia may be in violation of 230-24(a) {my extraced quote follows}:
"...The vertical clearance above the roof level shall be maintained for a distance of not less than 3 ft (914mm)
in all directions from the edge of the roof. (my bold added)
I realize (before the flaming starts,)
![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
that the reference in 230-24(a) is
above but it also says
in all directions from the edge of the roof. Another example of doublespeak in the Code, perhaps? In any event, it looks to be too close to the facia.
Reading further, Art 230-26, Point of Attachment seems to apply too.
Good call on the red tag. But I wonder what would be the best way to correct this, short of relocating the meter?
(edited to add smiley)