I got a violation notice on a ground bar. (The picture I took of it came out bad, though, so here's one just like it).
I slipped up and told the inspector he was crazy...Oooops [Linked Image]
It's a factory supplied component for a Cutler-Hammer 225 Amp Main Lug panel.
Now, what's the matter with it?
#118251 08/17/04 08:14 PM
Hello Scott,
doesn't that come under the heading of s---happens? [Linked Image]
The only thing I can think of is he wants a green screw or nut.
Of course you could tell him that besides his being crazy, until a conductor is landed on the bar it doesn't exist. [Linked Image]
Roger
#118252 08/17/04 08:50 PM
What doesn't he like about it?
If this was a factor installed bar wouldn't any changes you make to it possibly void the UL listing?
I think you were being nice. I would have said more than calling him crazy.
Curt
Curt Swartz
#118253 08/17/04 09:50 PM
e57 Offline
Some people have a hair across it, and should be told so! (politely of course...)
Raise one brow like Spock, and a calm monotone voice... "I'm sorry, but you are out of your mind"
I had a simular thing happen with a panel once, the Inspector made some wild claim about "modification" of a neutral buss. So we continued with the Inspection, while I sent a guy to the supply house to get another one. He came back, we opened the un-opened box in front of him. Then took it back, a waste of time and money......
#118254 08/18/04 11:48 AM
Scott,
Was it a new, overly zealous inspector that I might be dealing with in a coastal city?
I've got one that wrote a subpanel I changed up as this exactly "Continuity problem at subpanel"
Thats all he wrote! [Linked Image] I called him & he said between the neutral & ground there's a continuity problem... I measured it & it rang out just fine... I recalled him out.... We'll see if he's really crazy [Linked Image]
-Randy
#118255 08/18/04 07:29 PM
The reason he wrote it up is that this mounting does not provide "direct metal contact."
He also doesn't like the EMT fittings without a grounding bushing or a Meyers Hub.
He says that the hole (7/8", 1-1/8", etc) is larger than the fitting, and thus does not provide "direct metal contact".
I looked up "direct metal contact" in the '99 NEC for a total of 0 hits for my query.
The secondary conductors from the utility transformer were not yet installed, so when I gave him a torque letter from the office that the gear had been torqued to specs, he told me I was committing FRAUD.
This & more was all before I told him he was crazy. [Linked Image]...S
He's an older fellow not by the beach, Randy.
#118256 08/18/04 07:45 PM
U
LMFAO!!!! [Linked Image]
Inspectors??? [Linked Image]
#118257 08/18/04 07:58 PM
I see it, its that ag, with the green writing, its partly under the attachment nut. It must be interfering with the "direct metal contact".
Or was that direct mental defect?? [Linked Image]
#118258 08/18/04 08:14 PM
I will steal a line from electricmanscott.
"Poor fellow"
Did you explain to him that no one gives a .... about what he likes?