Who's Crazy? #118250 08/17/04 07:57 PM
Joined: Dec 2000
Posts: 4,283
electure Offline OP
Member
I got a violation notice on a ground bar. (The picture I took of it came out bad, though, so here's one just like it).
I slipped up and told the inspector he was crazy...Oooops [Linked Image]


[Linked Image]

It's a factory supplied component for a Cutler-Hammer 225 Amp Main Lug panel.

Now, what's the matter with it?

Tools for Electricians:
Re: Who's Crazy? #118251 08/17/04 08:14 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Hello Scott,
Quote
I slipped up and told the inspector he was crazy...Oooops [Linked Image]
doesn't that come under the heading of s---happens? [Linked Image]

The only thing I can think of is he wants a green screw or nut.

Of course you could tell him that besides his being crazy, until a conductor is landed on the bar it doesn't exist. [Linked Image]

Roger

Re: Who's Crazy? #118252 08/17/04 08:50 PM
Joined: Apr 2002
Posts: 558
C
caselec Offline
Member
What doesn't he like about it?

If this was a factor installed bar wouldn't any changes you make to it possibly void the UL listing?

I think you were being nice. I would have said more than calling him crazy.

Curt


Curt Swartz
Re: Who's Crazy? #118253 08/17/04 09:50 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Some people have a hair across it, and should be told so! (politely of course...)

Raise one brow like Spock, and a calm monotone voice... "I'm sorry, but you are out of your mind"

I had a simular thing happen with a panel once, the Inspector made some wild claim about "modification" of a neutral buss. So we continued with the Inspection, while I sent a guy to the supply house to get another one. He came back, we opened the un-opened box in front of him. Then took it back, a waste of time and money......


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Who's Crazy? #118254 08/18/04 11:48 AM
Joined: Feb 2004
Posts: 1,432
Lostazhell Offline
Member
Scott,
Was it a new, overly zealous inspector that I might be dealing with in a coastal city?
I've got one that wrote a subpanel I changed up as this exactly "Continuity problem at subpanel"
Thats all he wrote! [Linked Image] I called him & he said between the neutral & ground there's a continuity problem... I measured it & it rang out just fine... I recalled him out.... We'll see if he's really crazy [Linked Image]

-Randy

Re: Who's Crazy? #118255 08/18/04 07:29 PM
Joined: Dec 2000
Posts: 4,283
electure Offline OP
Member
The reason he wrote it up is that this mounting does not provide "direct metal contact."


He also doesn't like the EMT fittings without a grounding bushing or a Meyers Hub.
He says that the hole (7/8", 1-1/8", etc) is larger than the fitting, and thus does not provide "direct metal contact".

I looked up "direct metal contact" in the '99 NEC for a total of 0 hits for my query.

The secondary conductors from the utility transformer were not yet installed, so when I gave him a torque letter from the office that the gear had been torqued to specs, he told me I was committing FRAUD.

This & more was all before I told him he was crazy. [Linked Image]...S


He's an older fellow not by the beach, Randy.

Re: Who's Crazy? #118256 08/18/04 07:45 PM
Joined: Jul 2004
Posts: 200
U
uksparky Offline
Member
Quote
Some people have a hair across it, and should be told so!

LMFAO!!!! [Linked Image]

Inspectors??? [Linked Image]


If hindsight were foresight, we'd all be millionaires!
Re: Who's Crazy? #118257 08/18/04 07:58 PM
Joined: Sep 2003
Posts: 123
M
mvpmaintman Offline
Member
I see it, its that ag, with the green writing, its partly under the attachment nut. It must be interfering with the "direct metal contact".

Or was that direct mental defect?? [Linked Image]

Re: Who's Crazy? #118258 08/18/04 08:14 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Quote
He also doesn't like the EMT fittings without a grounding bushing or a Meyers Hub.

I will steal a line from electricmanscott.

"Poor fellow"

Did you explain to him that no one gives a .... about what he likes?


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,069 Are you busy
205,048 Re: Forum
193,177 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3