0 members (),
164
guests, and
12
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2000
Posts: 3,682 Likes: 3
OP
Administrator Member
|
I went out to troubleshoot some tennis court lighting at a LARGE house & was curious why I was getting 240V between ground & neutral! I'll let the pics explain themselves.. Gotta love the mounting job on the sealtite! -Randy
|
|
|
|
Joined: Feb 2004
Posts: 74
Member
|
Let me take a guess, that neutral which is spliced in the panel came loose, or was the bonding screw, which bonds the neutral to the panel left in by mistake.
[This message has been edited by CRM (edited 05-24-2004).]
|
|
|
|
Joined: Feb 2004
Posts: 1,438
Member
|
CRM.... I opened a jbox down the line from here & noticed my hotstick lit up on the white & green wires... metered them & got 240V... Someone didnt seem to understand what colors to use for hots when this was installed!
-Randy
|
|
|
|
Joined: Mar 2004
Posts: 391
Member
|
When I saw these photos my code book just burst into flames.
Randy,
Do you know who in the world did that work? What were you trouble-shooting?
Is that undersized green conductor being used as the line-side neutral? Where are any EGCs? Where's the equipment ground bus?
-John
[This message has been edited by BigJohn (edited 05-24-2004).]
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
The mis-use of colors is a concern but what really worries me is I see no grounding conductor heading out the LT.
Or do I see a black 12 AWG as the grounding conductor for 30 amp circuits?
[This message has been edited by iwire (edited 05-24-2004).]
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Mar 2004
Posts: 98
Member
|
Good one Bigjohn,code book burst into flames!lol Yea,that job looks like home owner Bob and shade tree neighbor job, I`ll bet his wife was impressed though.My hubby can do anything,Dont you just love it.
|
|
|
|
Joined: Mar 2004
Posts: 98
Member
|
Oh and I forgot to mention the free advice from the Home depot dude.
|
|
|
|
Joined: Mar 2001
Posts: 333
Member
|
The line EGC is the smaller green conductor landed on the neutral bar . The line grounded conductor(unidentified)is the one spliced with the blue wire nut . The load grounded conductors are also black . Green and white ungrounded load conductors . At least the panel is a Square D (Homeline?).
Steve
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
Just how much lighting is out there, that needs two 30A 240V circuits plus another 120V circuit? (Is that 20A on the single-pole breaker? Can't quite make it out on my monitor.)
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Randy, Where were the conductors landed on the load side? It seems like anyone with the smarts to use the oversize conductors should have had the smarts to know about the grounding/grounded conductor stuff. Homeline is the "Premier" brand available at our Home Depots, BTW.
Bob, Most of the 3/4" LTFMC we use is listed as an equipment grounding conductor up to 60 Amps, 1/2" to 20 Amps.
|
|
|
HCE727
Delaware County, PA, USA
Posts: 187
Joined: November 2005
|
|
|
|