'99NEC 300-3
(c) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
Exception: For solar photovoltaic systems in accordance with Section 690-4(b).
FPN: See Section 725-54(a)(1) for Class 2 and Class 3 circuit conductors.
I have used 12" x 12" trough and
just bought extra ends for it so I
could make separate compartments in it.
Bob,
Does this make it not a wireway??
In the past, Tom, one of our members, has brought up the idea of a "custom made box" with the same dimensions as the wireway.
So, what would be the
real difference between a wireway with 50 conductors in a cross section, or a box with 50 conductors in a cross section??
[This message has been edited by electure (edited 04-21-2004).]