Pool + Shower Locations #116001 01/28/04 10:32 PM
Joined: Oct 2000
Posts: 3,631
Admin Offline OP
Administrator
Member
[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]
Quote
i have here two 'occupied' unfinished places, one is a pool with bathing suits hung off xmas lights, the other a shower in use w/o the glass door & wall.

these were taken the same day, different jobs

~Steve aka sparky

Tools for Electricians:
Re: Pool + Shower Locations #116002 01/29/04 05:24 AM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline
Member
That switch/receptacle box seems rather close to the shower area for my liking, even if it is a GFI outlet.

The temporary light spliced into the fixture box (last pic, upper right) is a nice touch!

Re: Pool + Shower Locations #116003 01/29/04 07:42 AM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
the sw/gfi location is to have a glass wall, the 3' rule will be met when it is installed.

my state (Vermont) does not have , for single family dwellings, occupancy permits.

so people tend to live with pigtails, or as situations seen here for indefinite periods of time...

where i stand as an EC here is worrisome,to energize or not energize is often the Q

~S~

Re: Pool + Shower Locations #116004 01/29/04 01:05 PM
Joined: Aug 2002
Posts: 35
S
strangedog Offline
Member
Even if the GFCI trips the wires in the open box are still hot (the line side). Don't reach for that switch from the shower or it will be the last thing you do! [Linked Image]

SD


SD
It is best for a leader to be both feared and loved. But since this usually cannot be done, it is safer to be feared.
Re: Pool + Shower Locations #116005 01/29/04 02:14 PM
Joined: Nov 2000
Posts: 246
R
rmiell Offline
Member
What 3' rule? There is no such rule for receptacles. See Section 406.8(C). Inside the space, sure, but where does the space end? 3' out? I don't think so. The bathtub and shower space stops at the end of the bathtub (or shower floor).

Rick Miell

Re: Pool + Shower Locations #116006 01/29/04 06:54 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
Thank you Rick
i have obviously confused 550.13(F)here with a normal residency

Re: Pool + Shower Locations #116007 02/25/04 03:01 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
There used to be what was refered to as the "3' rule" for outlets near sinks and the like, to be GFI'ed. It may have been re-worded, or moved in the Code. It was pretty early in the GFI requirements. I'm sure that was what Sparky was refering to, as it read very simular to that other code in motor homes.

Now get this, where I'M at... ( S.F. CA - That's right, we publish our own Code Book here, welcome to the City. And all ten Inspectors interpit it differently. ) You can get hit by the AHJ for for "within reach of the tub", to be GFI'ed. This goes for line side of a switch, sconces or fixtures below 8', and of course, outlets. ( You'll only get hit on it if it's really obvious. ) After dealing with some "San Fiasco's", you get frustrated. So, I go through this everytime I do a switch, or light near a tub. I say to myself, " F%#*, GFI the WHOLE Bathroom. At the Breakers!"

Here's another good example of a "San Fiasco":

120/240 volt 3-phase delta circuits - “A” phase black, “B” (high leg) phase PURPLE, “C” phase red;


[This message has been edited by e57 (edited 02-25-2004).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: Pool + Shower Locations #116008 02/25/04 06:19 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
Who cuts the cover plate for the switch/ receptacle?


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
BigB 2
Popular Topics(Views)
270,998 Are you busy
205,003 Re: Forum
193,120 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3