I have a question. Does the N.E.C allow splicing in LBs, can it be used as a general purpose junction box?
If yes, then I would call this "use of an LB as a juction box". This would bring up issues of internal box volume and maximum box fill. Removing the cover would probably reveal a code violation in these areas.
If No, then I would call this "modification of electrical equipment".(modifying a 2"LB to a 2"LB,LL3/4")
Does the N.E.C allow modification of electrical equipment without it being re-certified?
Crash, an LB(conduit body) can contain splices, but the body can't be modified. The conduit body cubic inch capacity must be marked by the manufacturer in order to splice in it.
I assume a special box is already sold for that type of configuration or a reducing connector? Or do you feed the fat pipe into a junction box first to tap into the thinner pipe and then from the box to the elbow?
If not....how would you go about puting something like this together properly?
Asking out of curiosity, not that I'm going to actually go out and do this for someone....
What article of the NEC does that violate? We drill holes in other boxes, etc. If it doesn't overstuff the LB, it doesn't seem like a bad move to me...can somebody educate me on this one?