#113765 09/27/02 08:38 PM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
This is a common situation. This is the riser for an underground Residential Service where the EMT has rusted away at and below ground level. Any Comments or Advice?

[Linked Image]

[This message has been edited by Webmaster (edited 09-27-2002).]

Joined: Apr 2002
Posts: 53
C
Member
Show the home owners an mpeg file of a transformer blowing up.

Call an electrician!

I would also say the soil seems slightly acidic [Linked Image]

To prevent this from happening one I would fasten a tin ingot to the EMT below soil level. This would provide the same protection as the anode on a hot water tank.

Of course, at this stage Plastic is the way to go to replace this and prevent it from happening again.