<img border="0" src=&q...uot;300" height="400">

<font face="Arial" size="2">Click Photo for a closer look</font>


Three phase main lug only panelboard is fed from a single phase service

panelboard 30 ft. away. A 100 Amp. three pole breaker in the single
phase

panelboard is protecting feeder conductors and sub panel.
Frank Cinker

Pittsburgh, PA.

Software for Electricians

Software for Electricians, Installers & Maintenance Technicians

Joined: Oct 2000
Posts: 5,393
S
Member
So..would this be the infamous "Delta Breaker" in 384-16-f ?

Joined: Dec 2000
Posts: 84
C
Member
Sparky,

You are correct. I presented this code violation in a previous post. (Code Forum) I thought I would send a photo of the sub-panel. As you can see at a glance, it looks perfectly legal. (Without taking voltage readings) Once the Inspector had the service panelboard cover removed the code violation was quite obvious.

Frank (cinkerf)

Joined: Oct 2000
Posts: 5,393
S
Member
Frank;
The Delta breaker deal has been, to my knowledge, a no-no for 2 or 3 decades.

There is confusion as to how the introdution of a third leg ( or in this case 2-A legs, 1-B leg ) was accomplished, simply because nobody is going to advertise this .

This makes it something of a curious oddity to newer trade members as I , who have really only been seriously involved at it since the mid-80's

Perhaps you could give us a little history thread on this sometime here?

PS- I wonder if that 2-pole GFI would work on A+A phase ??
[Linked Image]

[This message has been edited by sparky (edited 02-19-2001).]

Joined: Oct 2000
Posts: 4,161
Likes: 5
Member
Sparky,

Frank said that a 3pole 100a breaker was in the singlephase panel that fed this. That's where the 3 wires come from - ABA or BAB sequence I would assume.

Bill


Bill
Joined: Dec 2000
Posts: 38
T
Member
Sparky go to electricalzone.com click on
article search and type delta breaker.If I can think of any more references I will keep you posted.

Joined: Oct 2000
Posts: 5,393
S
Member
http://www.electricalzone.com/archive/search_display.asp?ID=19970201ecm

Delta breaker article, worth reading, thanks Rain
[Linked Image]

Software for Electricians

Software for Electricians, Installers & Maintenance Technicians

Joined: Oct 2000
Posts: 4,161
Likes: 5
Member


Bill
Joined: Oct 2000
Posts: 5,393
S
Member
Thanks Bill
[Linked Image]
This Delta deal is a well thought, but dangerous arangement