<p align="center"> <img border="0" src=&q...uot;400" height="300"> <p align="center"><font size="2" color="#FF6898">Click Photo for Larger Picture</font> Submitted by: ???? This picture was taken in the electrical room of an office building. The "electrician" decided to tap off the load side of this disconnect to feed a 100A load center under 10' away. He/she decided to use SEU for the feeder, routed through the LB cover.
[This message has been edited by Webmaster (edited 11-12-2000).]
I cannot figure out why someone would go to the trouble of cutting a hole in the LB cover to do this? Why wouldn't they just go directly to the switch through one of the unused ko's on the top of the switch? Is there something I'm missing?
The person who did this must have bid the job by the hour becasue of all the extra trouble they went to. I agree with Mr. Addis why not just use one of the unused k-o's??
There are more "little nasties" here. The flex running through the picture isn't strapped. Doesn't look like the 1/2" emt is either. The copper water lines look like they run right over the EXO. Bond wire in EXO is black. A real pro job from the beginning.