123.9 VAC drops to 122.4 ??? #11140
07/01/02 05:26 PM
07/01/02 05:26 PM
S
strainsa  Offline OP
Junior Member
Joined: Aug 2001
Posts: 3
After installing a new outside AC compressor the voltage at any outlet drops from 123.9 to 122.4 whenever the AC starts. This causes a momentary flicker in the household lights about 80% of the time. The AC company has installed a hard start capacitor with no change in the flicker. I had the utility company come out and they checked the voltage across the meter and saw the same thing. They said it is OK and within their specifications. Are they giving me a straight answer?

Work Gear for Electricians and the Trades
Re: 123.9 VAC drops to 122.4 ??? #11141
07/01/02 07:33 PM
07/01/02 07:33 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
I believe they can give you plus or minus 10% of nominal. So, If nominal is 120V then the math looks like 108-132V. How big is the service, how bid is the compressor?
It might also be an undersized service or service conductors. Have you completed a demand calc for this new load with the existing arrangement?


Ron
Re: 123.9 VAC drops to 122.4 ??? #11142
07/01/02 11:14 PM
07/01/02 11:14 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Sounds like superb voltage regulation. ANSI limits are ~110-127, and these numbers are in most utility and appliance manufacturer boilerplate.

Incandescent lamp flicker can be very difficult to subvert, for the human eye is very sensitive to it. Looks like everything is up to snuff and then some.

Re: 123.9 VAC drops to 122.4 ??? #11143
07/02/02 05:58 AM
07/02/02 05:58 AM
T
Trainwire  Offline
Member
Joined: Mar 2002
Posts: 360
Strasburg,PA,USA
Join the club, Ihave the same problem with My AC. When I had the 200 amp panel, meterbase and service entrance put in, the poco didn't bother to change the drop off the pole, so I have 2awg drops feeding a 4/0 service entrance, in the summer time when the other 2 houses on the transformer are running their ac too, I get a very pronounced flicker.
This is the ac's third season, so far so good.

Trainwire


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,329 Are you busy
187,955 Re: Forum
177,491 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.004s) Memory: 0.9601 MB (Peak: 1.0927 MB) Zlib enabled. Server Time: 2018-10-17 11:48:54 UTC