123.9 VAC drops to 122.4 ??? #11140 07/01/02 05:26 PM
Joined: Aug 2001
Posts: 3
S
strainsa Offline OP
Junior Member
After installing a new outside AC compressor the voltage at any outlet drops from 123.9 to 122.4 whenever the AC starts. This causes a momentary flicker in the household lights about 80% of the time. The AC company has installed a hard start capacitor with no change in the flicker. I had the utility company come out and they checked the voltage across the meter and saw the same thing. They said it is OK and within their specifications. Are they giving me a straight answer?

Work Gear for Electricians and the Trades
Re: 123.9 VAC drops to 122.4 ??? #11141 07/01/02 07:33 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
I believe they can give you plus or minus 10% of nominal. So, If nominal is 120V then the math looks like 108-132V. How big is the service, how bid is the compressor?
It might also be an undersized service or service conductors. Have you completed a demand calc for this new load with the existing arrangement?


Ron
Re: 123.9 VAC drops to 122.4 ??? #11142 07/01/02 11:14 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
Sounds like superb voltage regulation. ANSI limits are ~110-127, and these numbers are in most utility and appliance manufacturer boilerplate.

Incandescent lamp flicker can be very difficult to subvert, for the human eye is very sensitive to it. Looks like everything is up to snuff and then some.

Re: 123.9 VAC drops to 122.4 ??? #11143 07/02/02 05:58 AM
Joined: Mar 2002
Posts: 360
T
Trainwire Offline
Member
Join the club, Ihave the same problem with My AC. When I had the 200 amp panel, meterbase and service entrance put in, the poco didn't bother to change the drop off the pole, so I have 2awg drops feeding a 4/0 service entrance, in the summer time when the other 2 houses on the transformer are running their ac too, I get a very pronounced flicker.
This is the ac's third season, so far so good.

Trainwire


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,710 Are you busy
204,950 Re: Forum
193,056 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3