ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#111282 10/08/06 12:33 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
A fast-food place called me, complaining that they kept losing power to their deep-fryers. FWIW, it turned out that the fryers were gas, and used electirc only for the controls and igniters.

I know why they were losing power; anyone out there care to guess?

[Linked Image]


For a closer look:

[Linked Image]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#111283 10/08/06 02:51 PM
Joined: Sep 2006
Posts: 23
E
Member
And they probably thought they were helping theirselves out. I cant stand those kind of calls, good cash but messy and busy to work around.

#111284 10/08/06 02:56 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
That is a problem as non-dwelling kitchens require GFCI protection.

Sounds like they have a problem with the equipment if it's tripping the GFCI.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#111285 10/08/06 04:06 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
Well, I suppose I ought to explain some about this install.

First of all, the fryer cords connect outside of the hood. This means that they will NOT be turned off when the Ansul system is operated.

The immediate problem, though, is the presence of the cord connections and GFI unit just above the fryers. When food is placed in the fryer, a great deal of moisture / oil enters the air. This will then condense on anything in it's path that is cooler. TRhat would include "cold" electrical connections.

Condensing moisture would allow current to leak across the face of the plug, to both the neutral and ground prongs. The GFI would see this, and trip.

Simply re-locating the connection outside of the condensation area eliminated the problem. (Of course, this was done without using extension cords, etc.)

None of the electric has been tied into the Ansul as yet; a bid has been submitted.

#111286 10/09/06 07:40 PM
Joined: Jun 2005
Posts: 821
S
Member
If condensation is causing current to "leak" from the receptacle, why not just install a GFCI OCPD as required by 210.8 (B) (2)?

(I love using those big electricial abbreviations)

#111287 10/09/06 07:42 PM
Joined: Jun 2005
Posts: 821
S
Member
Oh wait... that wouldn't solve the problem.

My bad.

#111288 10/09/06 07:47 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
John as these are 120 volt 20 amp circuits they can not provide the source of heat to the appliances.

It's not the power under a hood that must be killed it is the source of heat.

If these are Gas appliances a cable operated gas valve is in order.

At least that is how it's done in my area.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#111289 10/09/06 09:08 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
I've only installed a few "Ansul" systems, Iwire, so I am no expert. However, here it is required, when the system is tripped, that ALL sources of ignition be disconnected, as well as make-up air be stopped. This meands that the lights under the hood, any receptacles, and all electric equipment be shut off- in addition to the gas being shut off.

You are quite correct; the circuit only powered the controls and the gas igniter. Were these deep fryers to be all electric, they would likely need a 100 amp circuit. (Bit much for that extension cord!)

#111290 10/10/06 07:35 PM
Joined: Jun 2004
Posts: 220
T
Member
It is similar here, the last ansul I wired killed the make up air, the hood lights, and ran the exhuast fan for 30 seconds then shut it off. As the range was gas fired there was a cable operated valve that was tied into the trigger mechanism.

#111291 10/11/06 06:56 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Maybe I am wrong I will try to find the requirements.

As far as I can recall its not the source of ignition that needs to be killed....the ignition has already happened at the point the ansul trips.

But it is hard to extinguish a fire if heat is still being pumped into the bottom of the fire.

Remember the fire triangle Fuel, Oxygen, Heat.

I have never seen an Ansul system kill the under hood lights.


Bob Badger
Construction & Maintenance Electrician
Massachusetts