|
|
|
0 members (),
278
guests, and
11
robots. |
|
Key:
Admin,
Global Mod,
Mod
|
|
|
|
Joined: Oct 2000
Posts: 3,672 Likes: 4
OP
Administrator Member
|
This one was sent to me from another inspector in the office. The contractor also supported his rebar by driving pieces of bar into the earth and tying the horizontal pieces to them.
-Alan Nadon ![[Linked Image]](https://www.electrical-contractor.net/Forum/Images/Rebar_Conn.jpg)
|
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
Alan,
Is there a UL rebar clamp somewhere on that piece of rebar? Or is that ground wire just tie-wrapped to the rebar?
|
|
|
|
|
Joined: Nov 2002
Posts: 134
Member
|
What's that little mess on the right. Looks almost like someone tried to split the strands and wrap them around the rebar. Perhaps an underwriter's knot? ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif) RSlater, RSmike
|
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
The mess on the right is from seperating the strands and wrapping them around the rod. The nylon ties made a better connection although I don't think they are listed as direct burial connectors. ![[Linked Image]](https://www.electrical-contractor.net/ubb/biggrin.gif) Somedays it just doesn't seem like any progress is ever going to be made. Alan--
Alan-- If it was easy, anyone could do it.
|
|
|
|
|
Joined: Aug 2001
Posts: 466 Likes: 1
Member
|
While I would not accept that as an acceptable connection to the rebar, I would ask if the rebar was just supporting a 20' length of conductor would there need to be a connection?
|
|
|
|
|
Joined: Jun 2005
Posts: 91
Member
|
While I would not accept that as an acceptable connection to the rebar, I would ask if the rebar was just supporting a 20' length of conductor would there need to be a connection? I would say no.
-George
|
|
|
|
|
Joined: Jul 2002
Posts: 8,450 Likes: 4
Member
|
Alan, All that suggests to me is Galvanic Corrosion. Also them white cable ties will last about a month in the sun.
|
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
That sure looks like a 3/0 Ufer tied to the footer rebar.
Such is done all the time out my way.
The assembly to be puddled completely in concrete.
Zip ties or tie wire are used all of the time.
Normally no attempt is even made to get tricky at the end.
Tesla
|
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Same here, it is a conveinient way of suspending the GEC / UFER in the bottom in the pour. The guy probhably wrapped it at the end to get it to stay put while he rolled it out. The zip tie wont matter after preservation in the concrete... Any galvanic action is on the steel not the copper, and minimal at best. With current prices of copper you may see less of this type installation. Usually I try to go across the rebar, not along it....
[This message has been edited by e57 (edited 06-22-2006).]
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
Posts: 3,672
Joined: October 2000
|
|
|
|
|
|