More Hacking #109595
11/08/05 10:00 PM
11/08/05 10:00 PM
electure  Offline
OP
Member
Joined: Dec 2000
Posts: 4,271
Fullerton, CA USA
Submitted without a name:

I work at a newspaper office in central California. I am a computer
geek, not an electrican, but after seeing many of the scary photos on
the violation pictures forum, I was motivated to look around the old
building I work in to see if our 1930's-era structure had any dangerous
hazards, as it has been added-on to and had numerous modifications
throughout the years by countless people. I looked inside a crawl
space
and lo and behold, I found a major hack job right under our own roof --
not to mention a potential fire hazard. Also, other than the obvious
unsuspended NM cable, lack of a grounding conductor in the conduit,
overfilled junction box without a cover, and lack of wire nuts on the
splices -- do you notice anything else wrong with this picture? P.S.-
this mess has been in use for over 25 years!


[Linked Image]


[Linked Image]

2017 / 2014 NEC & Related Books and Study Guides
Re: More Hacking #109596
11/08/05 10:21 PM
11/08/05 10:21 PM
M
mamills  Offline
Member
Joined: Nov 2001
Posts: 745
Wharton, Texas, USA
Is it my monitor, or are all the wires the same color?

Mike (mamills)

Re: More Hacking #109597
11/08/05 10:32 PM
11/08/05 10:32 PM
B
BobH  Offline
Member
Joined: Oct 2004
Posts: 135
Newfane, N.Y USA
Picky, picky, picky. That mess has served well for 25 years and you're complaining! Emt can serve as the grounding conductor, the box doesn't look overfilled to me and who knows, there's probably crimp connectors under that tape. Looks like another beautiful job by an in-house maintenance mechanic.

Re: More Hacking #109598
11/08/05 11:34 PM
11/08/05 11:34 PM
Y
yaktx  Offline
Member
Joined: Feb 2003
Posts: 288
Austin, Texas, USA
Well, I wouldn't say it's a beautiful job, but I've seen worse. In Mexico, where all wires seem to be white, this would be first class. I don't see a ground connection on the NM-- that's a concern. Mighty thoughtful of the hacker to use NM connectors, though.

Quote
Emt can serve as the grounding conductor


Well, yes it can, but not if locknuts are missing (see the connector on top). It is always in the interest of safety to add a separate grounding conductor, as many jurisdictions now require. That way, when the maintenance guys do their worst, you might still have grounding continuity.

The box offsets in the EMT look nice. This was competently installed originally, before it was monkeyed with.

Re: More Hacking #109599
11/08/05 11:36 PM
11/08/05 11:36 PM
Y
yaktx  Offline
Member
Joined: Feb 2003
Posts: 288
Austin, Texas, USA
I dunno, I might be more inclined to worry about the pile of kindling stored under this box.

Re: More Hacking #109600
11/09/05 01:42 AM
11/09/05 01:42 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,236
SI,New Zealand
Mike,
Quote
Is it my monitor, or are all the wires the same color?

No worries with your monitor, mate, unless both of our monitors are broken.
Where did this cable come from?.
Seems like bargain basement stuff.
Quote
Emt can serve as the grounding conductor

My experience of metallic conduits, is that you never rely on any metallic conduits as part of the Fault Path.

Re: More Hacking #109601
11/09/05 02:40 AM
11/09/05 02:40 AM
W
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 787
Oradell NJ USA
Isn't there a rule against stringing romex thru the air like that?

Re: More Hacking #109602
11/09/05 04:21 AM
11/09/05 04:21 AM
N
newsgraphics  Offline
Member
Joined: Nov 2005
Posts: 11
California
I am the original poster, but I forgot to send my username in my email. I'm not an electrician, but I find numerous safety hazards and violations in this installation:

1. No wire nuts used to connect wires together (violation)

2. Ground wires on NM cable have been cut off and are not bonded to the conduit system (violation).

3. Overfilled 21 cu. in. metal junction box. (Violation) This box has a total of ten 12 ga. current-carrying conductors. For box-fill requirements, the code requries 2.25 cu. in per 12 ga. conductor. Add one extra conductor for the illegally cut-off ground wires on the NM cable, and the total is 11 conductors (2.25 x 11 = 24.75 Cu. In)

4. Ungrounded NM cable feeds 3 prong grounding-type ceiling outlets (violation), controlled by wall switch to power fluorescent lights in store room.

5. Use of white wire for hot conductor, without clear markings to differentiate from neutral conductor (violation).

6. Lack of grounding conductor, relying solely on conduit.

7. No cover on junction box, and wires protruding out of the box (violation).

8. Unsecured NM cable dangling through mid-air (almost certainly a code violation). NM cable use in commercial installation may be a violation as well.

[This message has been edited by newsgraphics (edited 11-09-2005).]

Re: More Hacking #109603
11/09/05 04:44 AM
11/09/05 04:44 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,236
SI,New Zealand
wa2ise,
Quote
Isn't there a rule against stringing romex thru the air like that?

Yeah, it's called lack of support. [Linked Image]

Re: More Hacking #109604
11/09/05 05:23 AM
11/09/05 05:23 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
My experience of metallic conduits, is that you never rely on any metallic conduits as part of the Fault Path.


Many times a properly installed metallic conduit system can provided a lower resistance ground path than the grounding conductor that would be installed inside it.

The NEC allows the use of many metallic raceways for grounding.

Quote
250.118 Types of Equipment Grounding Conductors.

The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more or a combination of the following:

(1)A copper, aluminum, or copper-clad aluminum conductor. This conductor shall be solid or stranded; insulated, covered, or bare; and in the form of a wire or a busbar of any shape.

(2)Rigid metal conduit.

(3)Intermediate metal conduit.

(4)Electrical metallic tubing.

(5)Flexible metal conduit where both the conduit and fittings are listed for grounding.

(6)Listed flexible metal conduit that is not listed for grounding, meeting all the following conditions:

a.The conduit is terminated in fittings listed for grounding.

b.The circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.

c.The combined length of flexible metal conduit and flexible metallic tubing and liquidtight flexible metal conduit in the same ground return path does not exceed 1.8 m (6 ft).

d.The conduit is not installed for flexibility.

(7)Listed liquidtight flexible metal conduit meeting all the following conditions:

a.The conduit is terminated in fittings listed for grounding.

b.For metric designators 12 through 16 (trade sizes 3/8 through 1/2), the circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.

c.For metric designators 21 through 35 (trade sizes 3/4 through 11/4), the circuit conductors contained in the conduit are protected by overcurrent devices rated not more than 60 amperes and there is no flexible metal conduit, flexible metallic tubing, or liquidtight flexible metal conduit in trade sizes metric designators 12 through 16 (trade sizes 3/8 through 1/2) in the grounding path.

d.The combined length of flexible metal conduit and flexible metallic tubing and liquidtight flexible metal conduit in the same ground return path does not exceed 1.8 m (6 ft).

e.The conduit is not installed for flexibility.

(8)Flexible metallic tubing where the tubing is terminated in fittings listed for grounding and meeting the following conditions:

a.The circuit conductors contained in the tubing are protected by overcurrent devices rated at 20 amperes or less.

b.The combined length of flexible metal conduit and flexible metallic tubing and liquidtight flexible metal conduit in the same ground return path does not exceed 1.8 m (6 ft).

(9)Armor of Type AC cable as provided in 320.108.

(10)The copper sheath of mineral-insulated, metal-sheathed cable.

(11)Type MC cable where listed and identified for grounding in accordance with the following:

a.The combined metallic sheath and grounding conductor of interlocked metal tape–type MC cable

b.The metallic sheath or the combined metallic sheath and grounding conductors of the smooth or corrugated tube type MC cable

(12)Cable trays as permitted in 392.3(C) and 392.7

(13)Cablebus framework as permitted in 370.3.
(14) Other electrically continuous metal raceways and auxiliary gutters listed for grounding.


The key is proper installation.

Regardless if you use a copper conductor or steel tubing as the EGC the ground fault path is only as good as the installers terminations.

We have all seen copper grounding conductors loosely twisted together with no wire nut.

It all comes back to the skill or care of the installer.

Many times I pull a wire grounding conductor, many times I do not and I sleep well knowing I tighten my fittings and support the raceway so it can not move loosening the joints. [Linked Image]

By the way the work in the photo stinks. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
248,569 Are you busy
186,287 Re: Forum
175,748 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.034s Queries: 15 (0.004s) Memory: 1.0324 MB (Peak: 1.2075 MB) Zlib enabled. Server Time: 2018-08-17 07:16:36 UTC