AE-Gifts, Affordable Everyday
0 members (), 160 guests, and 41 robots.
#105492 02/20/05 05:28 PM
What's Wrong With This Picture?
The clamp on the ground rod is 1/2 installed reversed, possibly because it is too large for the rod and would not tighten.
The ground clamp is backwards, the rod is not driven flush or below the ground level, and the GEC is not continuous to the ground rod
Look at page 5 of this pdf.
http://www.o-zgedney.com/PDF/MA1thru12.pdf
You can get UL listed reversible ground clamps. [Linked Image]
That water pipe clamp, even if it was turned around is not listed as a ground rod clamp. I also don't know where that copper strap came from.
Proper way would have been to use a GEC long enough to reach the ground rod and an acorn or other listed clamp.
-Hal
Hal that clamp may well indeed be listed for that use.
The two bumps touching the rod on the 'reversed' part of the clamp are a tip off.
From page 5 of the pdf link I posted above.
• GCA, GCH and GC-100-02B are
reversible for attachment to ground rods.
Bob
Bob, that's for a driven pipe grounding electrode, not a solid rod. [Linked Image]
-Hal
Was typing when you were. Ok, definite could be. [Linked Image]
-Hal
The rod clamp is rated to be used like this. I'd say the biggest violation here is the compression fitting that the Brass Conduit adapter is screwed on to. It could become loose in time.
Well thats my guess.
Rob
AM I the only one who considers this an improper means of splicing the GEC?