Electricians revenge
1 members (Scott35), 183 guests, and 10 robots.
#105199 07/10/04 07:09 PM
Iwire: Just how does a PVC bushing protect a wire from the edge of a PVC fitting?
#105200 07/10/04 07:34 PM
U
It's rounded - the chamfered edge of a rigid PVC can easily cut the softer sheath on cable [Linked Image]
#105201 07/10/04 07:50 PM
Maybe I have been misinformed, here is the code section I am thinking of. I do not see anything that says only metallic raceways.
I have always used bushings with PVC but that proves only that "I have always done it that way" [Linked Image]
part of 300.4(F)
(F) Insulated Fittings. Where raceways containing ungrounded conductors 4 AWG or larger enter a cabinet, box enclosure, or raceway, the conductors shall be protected by a substantial fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by substantial insulating material that is securely fastened in place.
How about it is there something I am overlooking? [Linked Image]
Bob
#105202 07/12/04 05:21 PM
Would the PVC conduit itself count as a "substantial insulating material that is securely fastened in place." ?
#105203 07/13/04 07:59 AM
The edge on the male adapter can be as sharp as a knife (I've shed the blood to prove it), or might be rounded.
Nonetheless, there's no exclusion for PVC.
It's a very normal thing to see PVC run into the bottom of stand up sections that's just cut off with no fitting whatsoever. That's what "bell ends" are made for. If you order them from the wholesaler, they will usually be a back ordered item, so rare is their use.
#105204 08/22/04 03:58 PM
Not only is there no exception in 300.4(f) for pvc but in 352.46 it requires bushings for any size wire when using pvc.
#105205 08/22/04 04:27 PM
I was failed on a temp service for forgetting one bushing. The whole service was pvc and needed eight bushings total. We miss counted and paid for it.
#105206 08/22/04 06:19 PM
Danson thanks for the lesson. [Linked Image]
I was not aware of 352.46 now I know I have been violating the code in smaller sizes of PVC. [Linked Image]
Bob