This is a service entrance conductor Drip Loop and has limitations according to the NEC.

What is the minimum distance to the "loop"?

[Linked Image]


Joe Tedesco, NEC Consultant
Horizontal Ad
#104620 09/10/03 05:49 PM
Joined: Aug 2001
Posts: 7,520
P
Member
At a quick code clook-up, I would think this is covered by 230.24(B).

Is there a messenger wire there? I can't see one, so I'm guessing that (1) wouldn't apply, and this drop would be covered by either (2) requiring a 12 ft. clearance or (4) requiring 18 ft. if there's truck traffic.

Have I missed anything?

#104621 09/10/03 06:45 PM
Joined: Aug 2001
Posts: 7,520
P
Member
OK, I think I misread that first time. Part (1) applies to the loop so the minimum is 10 ft.

How high is this loop? From an upstretched arm, I'd guess around 8 ft. ?