Two for One! #103443 08/01/02 05:34 PM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
[Linked Image]

Hey!

Cite the rules that are violated here!


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Two for One! #103444 08/01/02 06:34 PM
Joined: Apr 2002
Posts: 4
R
Randy Barnett Offline
Junior Member
Caught you Joe -- using one of my pictures, eh? Go ahead anytime!

Say, don't blame the electrician on this one. This work was done on an Air Force base after the final electrical inspection was completed. The irrigation contractor needed to get 120V to his irrigation box on the outside of the building (upper right). So, he found a way to get it done (ouch!).

When we saw the flexible conduit going into that elbow, we had to get a key to open the door and this picture is what we found!

Re: Two for One! #103445 08/02/02 07:43 AM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
Randy:

Whew! I was really worried, and didn't want any legal problems.

I too have many pictures and many people use them during their classes. I have no problem with that because I am the only one who has "the rest of the story"

Do you have any more pictures to share?

Quote
Say, don't blame the electrician on this one. This work was done on an Air Force base after the final electrical Inspection was completed. The irrigation contractor needed to get 120V to his irrigation box on the outside of the building (upper right). So, he found a way to get it done (ouch!).




[This message has been edited by Joe Tedesco (edited 08-02-2002).]


Joe Tedesco, NEC Consultant
Re: Two for One! #103446 08/02/02 10:44 AM
Joined: Jan 2002
Posts: 122
W
wirewiz Offline
Member
Violations:
110-2. Approval. The conductors and equipment required or permited by this code shall be acceptable only if approved.

547-13. Bends- How Made. Bends of rigid nonmetallic conduit shall be made so that the conduit will not be damaged and the internal diamater of the conduit will not be effectively reduced. Field bends shall be made only with bending equipment identified for the purpose, and the radius of the inner edge of such bends shall not be less than shown in table 346-10.

347-8. (a) Securely Fastened Each rigid nonmetallic conduit shall be securely fastened within 3 ft of each outlet box, junction box, device box, conduit body, or other conduit termination. Conduit listed for securing at other than 3 ft shall be permited to be installed in accordance with the listing.

What did I miss?
Wirewiz

Re: Two for One! #103447 08/10/02 09:59 AM
Joined: Oct 2000
Posts: 2,749
Joe Tedesco Offline OP
Member
wirewiz:

Good, and from the 1999 NEC, just change 547-13 to 347-13.


Joe Tedesco, NEC Consultant

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,710 Are you busy
204,951 Re: Forum
193,056 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3