Two for One!
#103443
08/01/02 05:34 PM
|
Joined: Oct 2000
Posts: 2,749
OP
Member
|
Hey! Cite the rules that are violated here!
Joe Tedesco, NEC Consultant
|
|
|
Re: Two for One!
#103444
08/01/02 06:34 PM
|
Joined: Apr 2002
Posts: 4
Junior Member
|
Caught you Joe -- using one of my pictures, eh? Go ahead anytime!
Say, don't blame the electrician on this one. This work was done on an Air Force base after the final electrical inspection was completed. The irrigation contractor needed to get 120V to his irrigation box on the outside of the building (upper right). So, he found a way to get it done (ouch!).
When we saw the flexible conduit going into that elbow, we had to get a key to open the door and this picture is what we found!
|
|
|
Re: Two for One!
#103445
08/02/02 07:43 AM
|
Joined: Oct 2000
Posts: 2,749
OP
Member
|
Randy: Whew! I was really worried, and didn't want any legal problems. I too have many pictures and many people use them during their classes. I have no problem with that because I am the only one who has "the rest of the story" Do you have any more pictures to share? Say, don't blame the electrician on this one. This work was done on an Air Force base after the final electrical Inspection was completed. The irrigation contractor needed to get 120V to his irrigation box on the outside of the building (upper right). So, he found a way to get it done (ouch!). [This message has been edited by Joe Tedesco (edited 08-02-2002).]
Joe Tedesco, NEC Consultant
|
|
|
Re: Two for One!
#103446
08/02/02 10:44 AM
|
Joined: Jan 2002
Posts: 122
Member
|
Violations: 110-2. Approval. The conductors and equipment required or permited by this code shall be acceptable only if approved.
547-13. Bends- How Made. Bends of rigid nonmetallic conduit shall be made so that the conduit will not be damaged and the internal diamater of the conduit will not be effectively reduced. Field bends shall be made only with bending equipment identified for the purpose, and the radius of the inner edge of such bends shall not be less than shown in table 346-10.
347-8. (a) Securely Fastened Each rigid nonmetallic conduit shall be securely fastened within 3 ft of each outlet box, junction box, device box, conduit body, or other conduit termination. Conduit listed for securing at other than 3 ft shall be permited to be installed in accordance with the listing.
What did I miss? Wirewiz
|
|
|
Re: Two for One!
#103447
08/10/02 09:59 AM
|
Joined: Oct 2000
Posts: 2,749
OP
Member
|
wirewiz:
Good, and from the 1999 NEC, just change 547-13 to 347-13.
Joe Tedesco, NEC Consultant
|
|
|
|
|