Push-ups or Jumping Jacks? #10195
06/01/02 07:34 AM
06/01/02 07:34 AM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I've noticed that many of the "Home Inspection Reports" related to real-estate transactions recommend "exercising" circuit breakers on a regular basis.
What are your thoughts?

Work Gear for Electricians and the Trades
Re: Push-ups or Jumping Jacks? #10196
06/01/02 08:03 AM
06/01/02 08:03 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,903
NY, USA
Redsy,

I've always thought the same thing and would probably bet that I've read it somewhere in mfgrs instructions or recommendations. I've seen a lot of times where someone will turn off their Main to do work (as recommended) and it will not reset, and I was thinking that 20+ years in one position in a damp basement can't be good for anything. [Linked Image]

Bill

Re: Push-ups or Jumping Jacks? #10197
06/01/02 09:01 AM
06/01/02 09:01 AM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,371
I had heard some years ago of a UL requirement to 'mechanically' operate breakers manually but have never verified this.

Re: Push-ups or Jumping Jacks? #10198
06/01/02 09:29 AM
06/01/02 09:29 AM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
I think it's a good idea to cycle breakers, maybe off and on a couple of times ar least once a year.

Re: Push-ups or Jumping Jacks? #10199
06/01/02 11:38 AM
06/01/02 11:38 AM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
That just happened to me last week. I swung by a friends to demo a floor box she didn't want before the new carpet was put down the next day. I figured I could squeeze it in before my final at school the same night. Rather that trace out which circuit I threw the main. On my way out I turned it back on and wouldn't you know it, the thing would not reset. I don't know if it was from not being exercised or if it just broke. It did not sound to good inside.

Re: Push-ups or Jumping Jacks? #10200
06/01/02 01:58 PM
06/01/02 01:58 PM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Outdoor discos mounted below OH meter bases are the worst... Especially when SEU cable and a "WP" hub is involved. I tend to shy away from switching any mains unless absolutely neccesary.

*crunch*


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Push-ups or Jumping Jacks? #10201
06/01/02 09:03 PM
06/01/02 09:03 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
66vdub-- sounds like a classic high-pucker-factor 'trap.'

Rambling Notes on circuit breakers after installation

NETA MTS-2001 7.6.1.1 Circuit Breaker INSPECTION PROCEDURES “Inspect ∙ Clean ∙ Operate the circuit breaker to insure smooth operation…”

{Factory-applied lubricants harden/leach. Do not use spray lube/cleaner unless it’s in CB maintenance instructions.}

Vaguely related links: http://www.nema.org/products/div5/5ab/guess.html http://www.seekandsource.com/news/Articlespec.Asp?Article_id=ARTI93 http://www.powellservice.com/PASD%20Test%20Procedures/TABLE%2010.7.doc http://www.ch.cutler-hammer.com/fred/cscpgh/fax/00000291.pdf http://www.ch.cutler-hammer.com/fred/cscpgh/fax/00000253.pdf http://www.ch.cutler-hammer.com/fred/cscpgh/fax/00000607.pdf http://www.ch.cutler-hammer.com/fred/cscpgh/fax/00000615.pdf http://standards.ieee.org/colorbooks/sampler/Bluebook.pdf


[This message has been edited by Bjarney (edited 06-02-2002).]

Re: Push-ups or Jumping Jacks? #10202
06/01/02 11:00 PM
06/01/02 11:00 PM
H
hurk27  Offline
Member
Joined: May 2002
Posts: 68
Portage, Indiana
does any body use nolox when you install a main or any other high amperage breaker on a buss that's aluminum. I have had many breakers fail because of this problem and have been using the nolox for some time.
:Wayne


Be Fair, Be Safe
Just don't be Fairly Safe
Re: Push-ups or Jumping Jacks? #10203
06/02/02 01:55 PM
06/02/02 01:55 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
hurk— Be Careful. That may be a misapplication if using particle-bearing inhibitor or any substance on the spring-clip/stab end of molded-case breakers. Conductive particles in sticky paste may incite carbon tracking and breakdown if left in contact with {bakelite} insulating surfaces.


[This message has been edited by Bjarney (edited 06-03-2002).]

Re: Push-ups or Jumping Jacks? #10204
06/03/02 06:01 AM
06/03/02 06:01 AM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
I've wiped a little nolox on meter stabs when I've had difficulty removing the meter.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Top Posters(30 Days)
djk 3
Popular Topics(Views)
251,688 Are you busy
188,815 Re: Forum
178,533 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.030s Queries: 15 (0.007s) Memory: 1.0259 MB (Peak: 1.2001 MB) Zlib enabled. Server Time: 2018-11-22 10:57:58 UTC