Whaaat size disconnect? #101240
02/26/07 07:51 PM
02/26/07 07:51 PM
renosteinke  Offline OP
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I really ought to already know the answer ... but I'd like to see your take on this issue.

An air conditioner is being installed. The A/C specifies that the circuit have a minimum ampacity of 28 amps, and a maximum OCPD (breaker) of 40 Amps.

The engineer has specified the 40 amp breaker, #8 wire, and a 30 amp disconnect.

In this situation - where the NEC allows for a larger breaker than usual - is it allowed to place a 30 amp disconnect on a circuit protected by a 40 amp breaker?

[This message has been edited by renosteinke (edited 02-26-2007).]

2017 / 2014 NEC & Related Books and Study Guides
Re: Whaaat size disconnect? #101241
02/26/07 08:24 PM
02/26/07 08:24 PM
S
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
440.12(A)(1)--115% of the nameplate rated load or branch circuit selection current, whichever is greater.

Most likely the 30amp disco will be ok. Also you only need number 10's for the conductors. There may be some voltage drop engineering invloved though.

Re: Whaaat size disconnect? #101242
02/26/07 10:31 PM
02/26/07 10:31 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
I suspect that you could be in trouble when you figure the HP rating of the 30a. disconnect against the HP rating of the AC. I would ask the responsible party to give me that information.

Edited to add- 28a. would equate to somewhere around 5 HP per T. 430.151A if I read correctly and I don't think a 30a. disconnect is rated that high. Please correct me if I'm wrong.

[This message has been edited by George Little (edited 02-26-2007).]


George Little
Re: Whaaat size disconnect? #101243
02/26/07 11:24 PM
02/26/07 11:24 PM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
440.12(A)(1)--115% of the nameplate rated load or branch circuit selection current, whichever is greater.

That tells me that 28 X 1.15 = 32.2 amps.

I'd use a 60 amp disconnect.

Plus there's more room in the 60.

Re: Whaaat size disconnect? #101244
02/27/07 08:11 AM
02/27/07 08:11 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
shockme,
Quote
440.12(A)(1)--115% of the nameplate rated load or branch circuit selection current, whichever is greater.
That tells me that 28 X 1.15 = 32.2 amps.

The 28 amps is the branch circit selection current and you are not required to take it at 115%. You use it at its face value.
Don


Don(resqcapt19)
Re: Whaaat size disconnect? #101245
02/27/07 09:35 AM
02/27/07 09:35 AM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,493
Michigan USA
Don- I agree with you about the sizing based on "branch circuit ampacity". I wonder what your thinking is about the horsepower thing?


George Little
Re: Whaaat size disconnect? #101246
02/27/07 09:49 AM
02/27/07 09:49 AM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
In which cases do I need to consider the 115%?

Re: Whaaat size disconnect? #101247
02/27/07 10:41 AM
02/27/07 10:41 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
George,
Quote
I wonder what your thinking is about the horsepower thing?

440.12(A) does not require a horsepower rating for this disconenct. As long as the ampere rating of the disconnect is equal to to or greater than the branch circuit selection current you are in compliance.
Don


Don(resqcapt19)
Re: Whaaat size disconnect? #101248
02/27/07 10:41 AM
02/27/07 10:41 AM
renosteinke  Offline OP
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Stupid attack on my part. oops.

Thanks, George, for reminding me of the horsepower ratings of the disconnect. I will be sure to mention this to the engineer involved. I do not expect that I will have trouble getting paid for the change order.

Re: Whaaat size disconnect? #101249
02/27/07 10:42 AM
02/27/07 10:42 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Shockme,
Quote
In which cases do I need to consider the 115%?

In those cases where the nameplate does not list a minimum circuit ampacity.
Don


Don(resqcapt19)
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 