ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 276 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 3 1 2 3
#101240 02/26/07 08:51 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
I really ought to already know the answer ... but I'd like to see your take on this issue.

An air conditioner is being installed. The A/C specifies that the circuit have a minimum ampacity of 28 amps, and a maximum OCPD (breaker) of 40 Amps.

The engineer has specified the 40 amp breaker, #8 wire, and a 30 amp disconnect.

In this situation - where the NEC allows for a larger breaker than usual - is it allowed to place a 30 amp disconnect on a circuit protected by a 40 amp breaker?

[This message has been edited by renosteinke (edited 02-26-2007).]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#101241 02/26/07 09:24 PM
Joined: Feb 2001
Posts: 308
S
Member
440.12(A)(1)--115% of the nameplate rated load or branch circuit selection current, whichever is greater.

Most likely the 30amp disco will be ok. Also you only need number 10's for the conductors. There may be some voltage drop engineering invloved though.

#101242 02/26/07 11:31 PM
Joined: Jan 2004
Posts: 1,507
G
Member
I suspect that you could be in trouble when you figure the HP rating of the 30a. disconnect against the HP rating of the AC. I would ask the responsible party to give me that information.

Edited to add- 28a. would equate to somewhere around 5 HP per T. 430.151A if I read correctly and I don't think a 30a. disconnect is rated that high. Please correct me if I'm wrong.

[This message has been edited by George Little (edited 02-26-2007).]


George Little
#101243 02/27/07 12:24 AM
Joined: Jun 2005
Posts: 821
S
Member
440.12(A)(1)--115% of the nameplate rated load or branch circuit selection current, whichever is greater.

That tells me that 28 X 1.15 = 32.2 amps.

I'd use a 60 amp disconnect.

Plus there's more room in the 60.

#101244 02/27/07 09:11 AM
Joined: Nov 2000
Posts: 2,148
R
Member
shockme,
Quote
440.12(A)(1)--115% of the nameplate rated load or branch circuit selection current, whichever is greater.
That tells me that 28 X 1.15 = 32.2 amps.
The 28 amps is the branch circit selection current and you are not required to take it at 115%. You use it at its face value.
Don


Don(resqcapt19)
#101245 02/27/07 10:35 AM
Joined: Jan 2004
Posts: 1,507
G
Member
Don- I agree with you about the sizing based on "branch circuit ampacity". I wonder what your thinking is about the horsepower thing?


George Little
#101246 02/27/07 10:49 AM
Joined: Jun 2005
Posts: 821
S
Member
In which cases do I need to consider the 115%?

#101247 02/27/07 11:41 AM
Joined: Nov 2000
Posts: 2,148
R
Member
George,
Quote
I wonder what your thinking is about the horsepower thing?
440.12(A) does not require a horsepower rating for this disconenct. As long as the ampere rating of the disconnect is equal to to or greater than the branch circuit selection current you are in compliance.
Don


Don(resqcapt19)
#101248 02/27/07 11:41 AM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
Stupid attack on my part. oops.

Thanks, George, for reminding me of the horsepower ratings of the disconnect. I will be sure to mention this to the engineer involved. I do not expect that I will have trouble getting paid for the change order.

#101249 02/27/07 11:42 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Shockme,
Quote
In which cases do I need to consider the 115%?
In those cases where the nameplate does not list a minimum circuit ampacity.
Don


Don(resqcapt19)