1 members (triple), 255 guests, and 15 robots.
#100852 01/12/07 09:16 PM
Hello Guys,
I am working in a commercial building, 200A 120Y/208V service. The meter is on the building, with the service conductors terminating in a 200A MB panel. Their is a 200A sub in the next stud pocket over fed from the main panel.
Here is the controversy. I asked for 5 runs of THHN to feed the subpanel, and the boss told me that it only needed 4 wires.
I asked him how you could make a load side connection to the grounded conductor, and he responded the inspector told him that because the panels where next to each other, the neutral and ground where bonded in the subpanel as well as in the main panel. Could anyone play devils advocate for me and tell me where I have gone astray?
Thanks, Gary
[This message has been edited by trekkie76 (edited 01-12-2007).]
Workgear for Electricians
#100853 01/12/07 10:23 PM
Ron Offline
Gary, you are correct. It should be a 5 conductor run for 3 phase 4 wire system plus ground. You are not permitted to have a n-g bond downstream of the main bonding jumper unless it is a separately derived source.
Ron
#100854 01/13/07 10:32 AM
If the wires are in metal conduit, you may not need a EGC per se, bonding would be through the conduit itself. How are the Phase conductors fed in the first panel? Do they come from a breaker or from the main breaker line side?
#100855 01/14/07 06:35 PM
The subpanel is fed from a 3 phase breaker on the load side of the main. I havent done anything yet, I was going to pipe it. If I used an acceptable metallic raceway I would not need an equipment ground, but I would still have to seperate nuetrals and grounds, correct? Can anyone think of a reason why the inspector would tell my boss such a thing?
#100856 01/14/07 07:33 PM
Tom Offline
If you run the feeder in a metal raceway, then all you need to do is keep the neutrals insulated from the enclosure and have a separate equipment ground bus.
Surely you have enough imagination to come up with a reason for the inspectors statement. I don't know about your area, but I know two around here that had former careers as CATV installer & the other one was a backhoe operator. With qualifications like that, they will occaisionally make a mis-statement about the NEC.
[This message has been edited by Tom (edited 01-14-2007).]
#100857 01/15/07 05:18 PM
Tom, Normally I would agree with you, but this guy has been an inpector for about 35 years!! He is very knowledgable, so something is not right. I am going to discuss this further with my boss tommorrow. Thanks all for your input, Gary
#100858 01/15/07 05:40 PM
I saw this 'short cut' once.....
As in this example, the panels were next to each other, with but a short nipple connecting them. The nipple was secured properly, with locknuts on both sides of the sheet metal.
Unfortunately, in the thirty years or so since the place was built, the connection was no longer as good as it once was. A little corrosion, a little vibration ... and the resistance of the connection increased. In effect, the nipple became a resistor.
Since the neutral was bonded to the case, the nipple was the only return path for unbalanced current. With the nipple no longer reliable, the "voltage to ground" varied greatly as loads changed during the course of the day.
Finally, one Thanksgiving holiday, the 'swing' in voltage became great enough to fry a large number of small surge suppressors. Looking at the circuits involved, all were powered from the same phase - though several circuits were involved. We looked and looked and looked - then realised what we were NOT seeing was any neutral wire to that panel!
I repaired this, and all was well. Indeed, the IT guys were astounded in all the mysterious power quality issues that went away! They had more fun with all their fancy scopes and meters than a kid on Christmas [Linked Image]
Since then, I've be a lot more focused on keeping my ground path and my neutral separated.
#100859 01/16/07 12:14 AM
I think you might be misunderstanding what they are telling you. Your fifth conductor is assumed to be a bonding conductor between the panels. If the panels are connected with the proper metallic nipple, locknuts, bushings, etc., this becomes the fifth (bonding) conductor. The other four become A,B,C and N.
The sub panel's neutral bar IS NOT bonded to the can.
Now, if you are using a non-metallic connection between the panels, then you'll need a fifh conductor for bonding.
The only exceptions to this are a few rare ones when dealing with detatched buildings.
---Ed---
#100860 01/16/07 01:08 AM
You just had the wrong IT guys or they had the wrong tools.
My Drainitz would have found that bad neutral in a minute or a foot of tape, whichever came first. [Linked Image]
#100861 01/17/07 05:35 PM
A little update, I asked the electrical instructor at the local tech college, who is very knowledgeable, and he said that because the panels are grouped together they are one service. He said it is in 230-70, which pretains to the six disconnect rule. I am unable to see how this applys, can anyone help?
