#100045 10/06/06 06:31 PM
Joined: Feb 2006
Posts: 78
L
Member
i am running a 1600 amp 120/208 volt 3ph service 300'underground, from a transformer to the building what size parallel wire is needed in alm.(and or in cu.)

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#100046 10/06/06 07:58 PM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
4 #600 cu kcm per phase = 420 x 4 = 1680.

#100047 10/06/06 09:34 PM
Joined: Feb 2006
Posts: 78
L
Member
Is that 600mcm cu. allowing for the voltage drop in 300'.

#100048 10/07/06 09:08 AM
Joined: May 2002
Posts: 1,716
R
Member
Duplicate thread, please go to the link below.
https://www.electrical-contractor.net/ubb/Forum1/HTML/007648.html

Roger