i am running a 1600 amp 120/208 volt 3ph service 300'underground, from a transformer to the building what size parallel wire is needed in alm.(and or in cu.)
Posted By: Bob Re: what size parallel wire - 10/06/06 11:58 PM
4 #600 cu kcm per phase = 420 x 4 = 1680.
Posted By: lite bulb Re: what size parallel wire - 10/07/06 01:34 AM
Is that 600mcm cu. allowing for the voltage drop in 300'.