Ok... I read 250.64(D)...which allows this arrangement.
But...would these taps to the 400 amp panels be of sufficent size to handle the ground-fault current that may be available from utility source?
Wouldn't the size of the main ungrounded service-entrance conductors(or equivalent size) in jsherrad's (which is a 1000 circular mills) and the neutral be capable of ground-fault current greater those taps can handle?
I thought that table 250.66 bases the size of the GEC according to the largest ungrounded service-entrance conductor for this reason
![[Linked Image]](https://www.electrical-contractor.net/ubb/confused.gif)
shortcircuit