Shortcircuit I don't know what to say.

I gave you the code as written, IMO it is quite clear.

Quote
(3) Bonding jumper(s) from grounding electrode(s) and grounding electrode conductor(s) shall be permitted to be connected to an aluminum or copper busbar not less than 6 mm x 50 mm (1/4" x 2").
The busbar shall be securely fastened and shall be installed in an accessible location. Connections shall be made by a listed connector or the exothermic welding process.


I took a picture of the 2005 IAEI Analysis of changes that illustrates this new code section. Sorry for the low quality.

[Linked Image]

Bob




[This message has been edited by iwire (edited 02-15-2005).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts