Sparky,
Is white with a red stripe legal for a neutral?
That is a good question. It appears to me that the stripe is only permitted for a "second system" grounded conductor. Is a grounded conductor for a second circuit a "second system"?
D) Grounded Conductors of Different Systems. Where conductors of different systems are installed in the same raceway, cable, box, auxiliary gutter, or other type of enclosure, one system grounded conductor, if required, shall have an outer covering conforming to 200.6(A) or 200.6(B). Each other system grounded conductor shall have an outer covering of white with a readily distinguishable, different colored stripe other than green running along the insulation, or shall have other and different means of identification as allowed by 200.6(A) or (B) that will distinguish each system grounded conductor.
Don(resqcapt19)
