Bob,
Don I am not trying to give you a hard time but I don't understand your position.
I just don't see a real reason not to install the welding secondary cable in a raceway. After looking at the code sections again, I think that you are correct that it would be a violation. I am not ready to completely agree, as welding cable is not listed in 400.4 so I am not sure that Article 400 applies. I really want to delete the last 7 words in 610.15 and say that the code does not apply to the secondary conductors of the welding equipment, but that will have to wait a few years.
Now you are just being argumentative.
If you haven't noticed before, I like to be that way.
Don