Ryan,
The IG conductor is in addition to the required EGC. So I'm not counting on the IG conductor to clear a fault, just its mythical job of reducing noise.
When I'm asked to provide an IG circuit, I provide an IG panel with an IG sized to match the EGC.
Since an IG is a design issue/choice, I don't think the NEC should get involved in the size.


Ron