Quote
If this is a 200amp service, there is no need to derate below 20amp for #12, 30amp for #10, 40amp for #8, and 50amp for #6.

Can you explain this?

The size of the service has no bearing on the rules of 310.15.


Bob Badger
Construction & Maintenance Electrician
Massachusetts