I think this gets down to the "bundling" question. If they fan out between bored holes this is a pretty thin beef. If the installer was very neat and they run in military precision I see the *potential* problem with the ones in the middle.
Rake them out with your fingers. Then they are not bundled. Twisted and kinked is a plus in this case.

It seems strange at first but "neat = heat".

The same thing is true in a panel when you see those "aircraft like" wire harnesses running down the gutters, tywrapped, with breaks at each device. It looks beautiful but derating can rear it's ugly head.


Greg Fretwell