210.52(A)(1) In every ... RECEPTACLE OUTLETS SHALL BE INSTALLED ....

210.70 ... LIGHTING OUTLETS SHALL BE INSTALLED ...

210.70(A)(1) exception No 1. In other than kitchens and bathrooms ...

(2)(a)&(c) Additional Locations

Article 100 - Receptacle outlet - An outlet where one or more receptacles are installed.

Even though there is no definition of 'lighting outlet', I believe the intent is similar as in receptacle outlet. Meaning the NEC expects some type of lighting luminaire/lampholder to be installed in the lighting outlet.

Since other locations in the NEC permit the installation of a switched receptacle outlet instead of a lighting outlet, I see that the kitchen, bathroom and stairway are required to have at least one luminaire/lampholder installed for the final inspection.


BTW: when one goes to the supply house, do they ask for a receptacle or receptacle outlet? [Linked Image]

Pierre


Pierre Belarge