It's an easy oversight… "E" in your formula is intended to be phase-to-phase balanced quantity. Your voltage measurements were from connecting a meter phase-to-neutral... 120V.

The cure is repetition, repetition, repetition.

A sanity check may be looking at the stator leads—thinking, "Are these more like 70-amp leads, or are they closer to 200-amp leads?"

Working with transformers and capacitors use the same calculations, but take time and experience to make sense.

Commit http://www.themeterguy.com/ohms%20law.jpg to memory, then beat into your head the cases where 3ø and square-root-of-3 apply.