Here is the skinny ...
We are using a generator and the book states the following but didn't show the amps:
120/208 vac - 60Hz
Load capacity: 60Kw
Power factor: .8
So to find out the amps I used: kWx1000/1.73xExPF
60000/1.73x208x.8
Amps = 208.42596
So my question is what is it? Is it 208 amps per phase or is it 208 split across the 3 phases for 69-70 amps per phase?
The reason that I ask this is because each phase is reading 120-124vac not 208vac.
Any input would be greatly appreciated.