Cliff,

Thanks for the info. As far as the why goes, maybe someone else can help with that. We generally must have a main OCPD within 5 feet of where the service conductors enter the house or must provide one outside. They will sometimes make some allowances depending on circumstances if it is well protected.

As far as the service conductors above the meter go they will balk at any part being hidden from view or enclosed in the building finish. I think that part of this is for fear that someone will tap into it before the meter. I have seen where this was done. A customer of mine bought a house from a utility employee some years ago. Where the service cable (SEU) passed through a 12 inch soffit the previous owner had tapped into it and soldered 40A fuses to the wires and continued to his Electric Stove. This was a 'Flying Splice' in the attic that I wish I could've caught on film. Though disconnected now, I think it is still there. [Linked Image]

You say that you have a 5 foot rule before OCPD? Is this in addition to the 10 feet that's in the riser already? That would make 15 if I'm understanding correctly [Linked Image]

Bill