I'm a little confused by something.

Quote
The compressor is 277/480

Assuming the compressor is 3Ø 3W, you don't utilize a neutral so there's really no 277V involved.

Assuming the compressor is 480V 3Ø 3W, and assuming it's not a dual voltage motor (480V 3Ø & 240V 3Ø), then with a 240V delta system I think you're pretty much looking at installing a transformer to match the supply voltage to the compressor.