What was the max size and number of conductors marked on the LB?

That is a real consideration.

A typical LB can not hold the same number of conductors as the raceway it is connect to.

A typical problem I run into is 225 amp feeders. We can run four 4/0 in 2" EMT but the 2" EMT LB is labeled as three - 4/0s max.

By the way TKB, how is BU I hear you have been a great help there and other places. [Linked Image]