A listed occupancy sensor with the equipment ground removed--Test Points are device yoke, and grounded switchbox.

What is the supply voltage, the meter shows 265? I question the validity also because this is a high impedance meter, you are probably measuring leakage. Put a resistance across the test points and it will go away.

-Hal