Sorry Ryan, could you explain the violation of 210.11(C)(1). I'm still not clear as to how it violates this code. 210.11(C)(1) states Small-Appilance Branch Circuits in addition to the number of branch circuits required by other parts of this section, two or more 20 amp small appliance branch circuits shall be provided for ALL receptacle outlets specified by 210.52(B)
If I'm reading 210.52(B)(3) correct it doesn't state this as being violated. It does mention that Additional small-appliance branch circuits shall be permitted to supply receptacle outlets in the kitchen and other rooms specified in 210.52(B)(1). No small-appliance branch circuit shall serve more than one kitchen. Exhibit 210.52 in the NEC 2005 handbook shows one of the branch circuits feeding the disposal.

[This message has been edited by Bert66 (edited 05-18-2005).]