Because they are both equipment fixed in place, neither of them would be permitted to consume more than 50% of the branch circuit rating (I am assuming 20 amps). Also, branch circuits must be sized to the load served, so you will have to add the rating of the two together and make sure it doesn't exceed the rating of the breaker.

210.19(A)(2)
210.20
210.23(A)(2)