A 16 AWG aluminum bonding wire is inside of, and in physical contact with, the metal armor providing a low-impedance fault return path required for the operation of overcurrent protection devices. The bonding wire is unique to AC cable and allows the outer metal armor in conjunction with the bonding wire to be used as an equipment ground. It is important to remember that the bare bond wire is not an equipment grounding conductor. It is the bond wire that, in combination with the interlocked metal armor, provides a low impedance equipment grounding path.
The purpose of this strip is to short together the turns of the spiral wrap, so fault currents won't turn the armor into an inductor, which can cause major heating and even fire.