[QUOTE]Originally posted by Tom:
[B]Fred,
I have yet to find a 1 gang plastic box that can handle the following scenario- three wire w/ground home run, 2 two wire cables & a receptacle. If there is a box big enough for this, my suppliers don't carry it.<<

Tom,
The box for what you described is a Carlon (or equiv) 32 cu. in. nail on 4S box, with a 1/2" mud ring. Works out to about 37 or 38 cu. in. total, I think.

In resi, we use #12 minimum for everything. Even lighting circuits, since the few homes we do a year are large customs with a lot of lighting. We try to get around voltage drop by using subpanels where we can.