I then checked the voltage with my trusty digital VOM- 15 volts...

This reading was nothing to worry about, a digital VOM reads induction from the other circuit, try the same measurement with analog meter.

I run many multiwire branch circuits and as long as you follow the rules that apply to them they work great, how many service entrance neutrals do you have? [Linked Image]

GFCIs do work down line from a multiwire branch circuit, not some times, every time.

Compare a GFCI fed from a multiwire branch circuit to a GFCI fed from a 2 wire branch circuit.

Once you get back to the panel it is the same thing, a common neutral.

One thing you can not do is protect outlets down line on a multiwire branch circuit with a GFCI outlet.

This is what electure and Electric Eagle where saying.