FYI guys. The code says you cannot use the gas pipe as an electrode, and you WILL bond it to the system. The bond can come from the piece of equipment likely to energize (all of which used to be in 250-80-(b) before they messed up 250).

A local jurisdiction in Va was requiring a separate ground rod to the gas UNCONNECTED to the service GEC, in other words isolated.

I won that fight about 5 years ago as far as VA is concerned. So in VA, you will bond it as per NEC, but you cannot use it as an electrode the way we used to.