What do you mean by "main conductor"?

Cu or Al?

Unless you calculated the maximum possible neutral load, how can you reduce the neutral size? And, even though reducing the neutral may be possible now, a good electrician will plan ahead for future neutral loads. There are, of course, plenty of cases where a reduced neutral is perfectly fine (a motor control center for example).