The copper waterline would still have to be bonded. (and 2 Gr rods - check local requirements) You have to think of it as putting all your metal stuff at the same potential which means that there would be no voltage there. If a live wire touched a pipe and it was not bonded it could remain live and breaker would not trip that would be bad for you standing outside in a puddle touching the water spigot.

The gas line may have different requirements, you better check on that. Maybe someone else can add more info here?