I for one do not recall seeing 600V rated thermostat wire for over 5 years. The only thing I have seen is rated for 300V. Since the insulation is not the same, it cannot be in the same raceway. 300.3(C)(1).
If some one ran 600V rated wire for the T-stat, it may be ok by code but IMO not very smart.


ed